View Full Version : Can you convert this air handler to R410a?



awfpack
04-26-2012, 08:32 PM
Can you change coils in this unit to take R410a?

Rheem Classic
Model: RHSA-HM4221JA
built: 12-2007
volts 208/240
single phase

Thanks

BaldLoonie
04-27-2012, 06:11 AM
Would have to braze in a new TXV.

awfpack
04-27-2012, 06:53 AM
So you are saying it can be done? Is the cost very high to do this?
Thanks

I have a bad HP that is R-22 and the air handler is r22. HVAC guy is checking to see if the AH could convert to R410a then install r410a HP.
Thanks for the help

gregp
04-27-2012, 08:58 AM
want to look into a dry-charged R-22 unit.

motoguy128
04-27-2012, 09:25 AM
Trying to convert the evap coil is not recommended. None on the lcoal contractors I've talked with will do it. Too hard to flush out all the incompatible oil from so many copper tubes.

The FYI there are 2 issues with coverting from R22 to R410a. 1) Pressure. 410 runs at a higher pressure so the coil would need to be rated for both. Many made after the mid 90's are. 2) oil - the oils used to lubricate the compressors that mixed with the refrigerant is icompatible and will contminate the special oil the R410a uses. If you don't flush it all out, the compressor won't live very long.

Go with a Dry fill. You should get 8-10 years without needing to add a significant amount of refrigerant if it's installed correctly. That's long enouhg where you'll be looking for a complete systme replaecment at that time.