View Full Version : Superheat and Subcooling
JAqu5545
04-23-2012, 08:36 PM
Hey,
I cant remember from last year but how do you know what your superheat and subcooling should be for 410a and R22 systems? Its been driving me nuts. Thanks guys
vstech
04-23-2012, 09:00 PM
system data plate, or installation instructions.
Dennis.Moore
04-25-2012, 01:20 PM
http://www.hvacfun.com/a-proper-resident-ac-charg-methods.htm
Most R-410A equipment utilizes TXVs and, therefore, you must charge them using subcooling. The recommended subcooling amount for R-410A is also 10° F to 15° F with a 3° F tolerance.
The days of grabbing the suction line with one hand and your crotch with the other then closing the charging valve when the pressure is to much to bear, are over :-)
JAqu5545
04-25-2012, 01:31 PM
On all new installs of 410a I run a QIV test for cool smart to make sure the refrigerant level, air flow, and voltages are all in an accetpable range. Thats exactly what they give you for a range. 3 degrees +\- the subcooling goal. They also want a superheat reading which i believe is +\- 5 or 7. The superheat goal is not on the nameplate like the subcooling. So I need to find out how to get the superheat goal. I think theres a chart out there I just need to find it. Thanks for the help
randyjoe
04-25-2012, 06:37 PM
SH=(3*IWB-ODB-80)/2
rdholder
04-25-2012, 07:52 PM
You can download this book it has a superheat chart, its FREE
http://shop.rdholder.com/Troubleshooting-an-Air-Conditioning-system-Troubleshooting.htm
FREE articles on Superheat, Subcooling and A/C Troubleshooting. For the FREE downloading of the articles go to Book and Papers on HVAC on the main page, put them in to the cart then, you must click on the PRINT AND CALL button for payment at check out. This method allows me to process your downloading at NO CHARGE.
JAqu5545
04-25-2012, 07:55 PM
I feel like that's a virus. Is that legit?
SolarMike
04-25-2012, 07:59 PM
http://www.hvacfun.com/a-proper-resident-ac-charg-methods.htm
Most R-410A equipment utilizes TXVs and, therefore, you must charge them using subcooling. The recommended subcooling amount for R-410A is also 10° F to 15° F with a 3° F tolerance.
The days of grabbing the suction line with one hand and your crotch with the other then closing the charging valve when the pressure is to much to bear, are over :-)
Sorry Dennis but I had too,:hijacked:
http://www.youtube.com/watch?v=qLkhx0eqK5w
Dennis.Moore
04-25-2012, 08:12 PM
Sorry Dennis but I had too,:hijacked:
http://www.youtube.com/watch?v=qLkhx0eqK5w
Your life or your lupines!:putergreet:This monetary redistribution concept is more difficult than I had imagined.
SolarMike
04-26-2012, 06:55 AM
Dennis Moore, Dennis Moore, steels from the rich and gives to the poor......lupines
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.