gseaquest
04-01-2012, 06:37 PM
I have been doing a lot of reading lately about restrictions and ran into system that I think may have a partial restriction. It is a lennox 3 ton packaged unit installed in 2009. Maybe you can learn me somethin. I will get the model number an more specifics later.
OAT 88/IDB 77/IWB 64/High 300/Low 90/Comp Amps 7.75/Evap coil clean/Blower operation normal/Speed High/RAT 77/SAT 62
WHen I opened the blower door I observed frost starting to build up on the tubes feeding the evaporator. After I waited a few the frost proceeded to develop on the evap coil. I thought i might be a partial restriction in the metering device but as a first step I added refrigerant to bring the operating pressures up. The pressures were just below manufactures specs after adding 3lbs 410. I checked the super and sub at the service connections. SH 30 SC 20. Hopefully this is enough for you guys to chew on for a few. I am going to grab a bit a will check back later and can provide more specifics.
OAT 88/IDB 77/IWB 64/High 300/Low 90/Comp Amps 7.75/Evap coil clean/Blower operation normal/Speed High/RAT 77/SAT 62
WHen I opened the blower door I observed frost starting to build up on the tubes feeding the evaporator. After I waited a few the frost proceeded to develop on the evap coil. I thought i might be a partial restriction in the metering device but as a first step I added refrigerant to bring the operating pressures up. The pressures were just below manufactures specs after adding 3lbs 410. I checked the super and sub at the service connections. SH 30 SC 20. Hopefully this is enough for you guys to chew on for a few. I am going to grab a bit a will check back later and can provide more specifics.