manowar
03-29-2012, 10:10 PM
Hello gentlemen, hopefully you can be of assistance to me.First let me list the equipment.
5 ton Carrier evaporator coil- cnrvt6024ataabaa
Originally internal 410a t x v, Converted to external r 22 t x v -4/5 tonnage-08`
Trane furnace-tuh2c100a9v4vaa-09`- all the literature I find says this should be a variable speed motor. But it is a standard 4 speed motor which is on the proper motor lead being the black wire for A/C.
4 ton trane condenser-2ttr2048a1000aa-05`
Now the symptoms- o/s ambient temp 85 I/s ambient temp 75. Charge:195/48 w/12 subcooling. Coil spotless and new filter. System is upflow in hallway closet,well sealed with plenty of return. Only getting 14 degrees temp split across system at coil.
I did this type of work 15 years ago, and I know for a fact I don't remember all of it. I did not do any of this work myself, it is in a house I just bought that supposedly passed inspection. Your input is greatly appreciated on a solution.
Thank you
5 ton Carrier evaporator coil- cnrvt6024ataabaa
Originally internal 410a t x v, Converted to external r 22 t x v -4/5 tonnage-08`
Trane furnace-tuh2c100a9v4vaa-09`- all the literature I find says this should be a variable speed motor. But it is a standard 4 speed motor which is on the proper motor lead being the black wire for A/C.
4 ton trane condenser-2ttr2048a1000aa-05`
Now the symptoms- o/s ambient temp 85 I/s ambient temp 75. Charge:195/48 w/12 subcooling. Coil spotless and new filter. System is upflow in hallway closet,well sealed with plenty of return. Only getting 14 degrees temp split across system at coil.
I did this type of work 15 years ago, and I know for a fact I don't remember all of it. I did not do any of this work myself, it is in a house I just bought that supposedly passed inspection. Your input is greatly appreciated on a solution.
Thank you