View Full Version : Stuck txv
Bigdtown
03-19-2012, 06:19 PM
So in ac my high side pressures were pretty normal, but my low side was about 30 psi (410 a system). All my spider legs are freezing up and so I took the bulb off of the suction and put a wet towel on it then I went back up to my guages and my low side was still sitting on 30psi, not hunting at all. I diagnosed a stuck txv. Do you agree?
Bigdtown
03-19-2012, 06:38 PM
wet, warm towel that is.
hvaclover
03-19-2012, 06:49 PM
sounds like to me
Milk man
03-19-2012, 07:26 PM
Yes. When you purged your high side hose, was there a lot of liquid.
Bigdtown
03-19-2012, 07:28 PM
yeah there was actually. Tons. the remnants of what the evaporator was storving for I presume.
freonrick
03-19-2012, 07:52 PM
what was your subcooling?
Bigdtown
03-19-2012, 08:03 PM
didn't check superheat or subcooling due to the fact that I couldn't get the txv to hunt. Probably should have but didn't. I can tell you that the high side was pretty much spot on for what Lennox said it should be.
freonrick
03-19-2012, 08:19 PM
your subcooling would have told you if you was stacking freon in the condenser or low on gas.
hvaclover
03-19-2012, 08:21 PM
Well, I would agree that while this is an obvious restriction based on the info you provided, a SH and SC check should always be performed.
Bigdtown
03-19-2012, 08:27 PM
I agree. That is only the second stuck txv that I have come across and will remember to do a sh and sc check next time and will in fact do one on this unit before I begin the work of changing it. I would think that the superheat would be more important to the diognosis than the subcool, am I wrong?
I always use a cup of warm water and ice water to see how the TXV reacts but I suppose a warm/ice cold wet towel would work and be a little bit easier to handle.
Bigdtown
03-19-2012, 08:32 PM
your subcooling would have told you if you was stacking freon in the condenser or low on gas.
oh, right on. good point. Thanks.
hvaclover
03-19-2012, 10:54 PM
I agree. That is only the second stuck txv that I have come across and will remember to do a sh and sc check next time and will in fact do one on this unit before I begin the work of changing it. I would think that the superheat would be more important to the diognosis than the subcool, am I wrong?
No, the SC is most important in this case...the evap is going to be starved and SH will be high...
Bigdtown
03-20-2012, 07:21 AM
No, the SC is most important in this case...the evap is going to be starved and SH will be high...
gotcha.
PM Heat n Cool
03-24-2012, 01:58 PM
Check superheat and subcooling....if both are high its most likely the txv or some kind of restriction
Sent from my SPH-D710 using Tapatalk
Bigdtown
03-24-2012, 08:07 PM
just a little update here...I checked subcooling and it was pretty much right on, as was my approach method. Suction was still sitting at 30psi so I went ahead and changed the TXV and after that the pressures were perfect. Don't really know why but it in this case it seems subcooling could not be trusted.